Motors Controls: Motor Branch

18 question stems · Page 1 of 1

Question 1

What is the main purpose of a disconnecting means installed within sight of a motor?

Question 2

In a low-voltage control circuit for lighting, why might a relay panel be used instead of switching line-voltage conductors directly at each switch?

Question 3

You need to check the continuity of a control circuit that is de-energized. Which instrument setting is most appropriate?

Question 4

You are tasked with selecting conductors and overcurrent protection for a single three-phase motor load. Which design approach is most appropriate?

Question 5

A small air compressor on a 15 A, 120 V circuit causes the breaker to trip occasionally at startup, even though the running current is only 9 A. What is the most appropriate solution?

Question 6

A 15 HP, 600V, 3-phase induction motor has a nameplate Full Load Amps (FLA) of 17A. What is the minimum ampacity rating for the branch circuit conductors?

Question 7

What is the maximum setting of a time-delay fuse used for motor branch circuit protection?

Question 8

A 15 HP, 600V, 3-phase motor has a nameplate Full Load Amps (FLA) of 17A. What is the minimum ampacity for the branch circuit conductors?

Question 9

What is the maximum time-delay fuse setting for a motor branch circuit?

Question 10

During troubleshooting, you find that a motor’s overload relay frequently trips after the motor runs for several minutes, even though the overcurrent device does not trip. What is the most likely issue?

Question 11

On a schematic for a motor control circuit, what does a dashed line connecting a contact to a coil usually indicate?

Question 12

In a motor starter, what is the primary function of the overload relay?

Question 13

You are troubleshooting a control circuit where a contactor coil does not energize. You measure control voltage on one side of the coil but not on the other. Which failure is most likely?

Question 14

A 2 hp, 240 V single-phase motor has a nameplate full-load current of 12 A. If the branch-circuit short-circuit and ground-fault protective device is sized at 250% of the motor FLC, what is the nearest standard overcurrent device rating?

Question 15

What is the primary function of a power distribution block (PDB) in a control panel?

Question 16

A $240\text{ V}$ motor is drawing $28 \text{ A}$ at full load. The motor is protected by a standard fuse rated at $175\%$ of the FLC. What is the maximum standard fuse rating permitted?

Question 17

A 10 hp, 3-phase, 480 V motor has a full-load current (FLC) of 14 A per its nameplate. For a continuous-duty application, which branch-circuit conductor ampacity is MOST appropriate when sizing conductors at 125 percent of the motor FLC (ignoring correction factors)?

Question 18

A 10 hp, 3-phase, 480V motor has a nameplate Full Load Amps (FLA) of 14A. What current value should be used to size the branch circuit conductors?